Hazardous Location Installation
Special Conditions for Safe Use:
ATEX
Intrinisically Safe
TAEI6000, TDEI6000 & TJEI6000 series with "W" Option
Ex ia IIC T4 Ga (Ta = -40°C to +70°C)
Ex ia IIIC T135°C Da (Ta = -40°C to +70°C)
TAEI6000, TDEI6000, TTEI6000 & TREI6000 series
Ex ia IIC T4 Ga (Ta = -40°C to +70°C)
IECEx
Intrinisically Safe
TAEI6000, TDEI6000 & TJEI6000 series with "W" Option
Ex ia IIC T4 Ga (Ta = -40°C to +70°C)
Ex ia IIIC T135°C Da (Ta = -40°C to +70°C)
TAEI6000, TDEI6000, TTEI6000 & TREI6000 series
Ex ia IIC T4 Ga (Ta = -40°C to +70°C)
FM
Intrinisically Safe
TAFI6000, TDFI6000
CL I, II, III, Div 1, Grps ABCDEFG
I/0 AEx ia IIC T4 Ga (Ta = -40°C to +80°C)
Type 3R Enclosure
Nonincendive
CL I, Div 2, Grps ABCD T4 (Ta = -40°C to +80°C)
Installation Entity IS and NI System Drawing 16984
Intrinisically Safe
TTFI6000 & TRFI6000
CL I, II, III, Div 1, Grps ABCDEFG T4 (Ta = -40°C to +80°C)
I/0 AEx ia IIC T4 Ga (Ta = -40°C to +80°C)
Nonincendive
CL I, Div 2, Grps ABCD T4 (Ta = -40°C to +80°C)
Installation Entity IS and NI System Drawing 16984
Intrinisically Safe
TAFI6000, TDFI6000 & TJFI6000 with "W" Option
CL I, II, III, Div 1, Grps ABCDEFG T4 (Ta = -40°C to +80°C)
I/0 AEx ia IIC T4 Ga (Ta = -40°C to +80°C)
Type 4 Enclosure
Nonincendive
CL I, Div 2, Grps ABCD T4 (Ta = -40°C to +80°C)
Installation Entity IS and NI System Drawing 16984
CSA
Intrinisically Safe
TTCI6000 & TRCI6000
II 1GD
CL I, Div 1, Grps ABCD T4 (Ta = -40°C to +80°C)
Exia per drawing 18005
CI I, Div 2, Grps ABCD
TACI6000 & TDCI6000
II 1G
CL I, Div 1, Grps ABCD T4 (Ta = -40°C to +80°C)
Exia per drawing 18005
CI I, Div 2, Grps ABCD
Type 3R
TACI6000 & TJCI6000 with "W" Option
CL I, II, III Div 1, Grps ABCDEFG T4 (Ta = -40°C to +80°C)
Exia per drawing 18005
CL I, II Div 2, Grps ABCDFG
Type 4
TDCI6000 with "W" Option
CL I, II, III Div 1, Grps ABCDEFG T4 (Ta = -40°C to +80°C)
Exia per drawing 18005
CL I, II Div 2, Grps ABCDFG
IP65
Table 1. Hazardous Location Wiring Practices
Country
U.S.
Canada
Europe
Intrinsically Safe Connections
Table 2. Intrinsically Safe Installation Drawings.
Limitations/Exceptions
6
Wiring in Hazardous Areas
Agency
FM
ANSI/ISA RP 12.6 & ANSI/NFPA 70
CSA
CEC Part 1
EN 50 039, EN 60079-14, IEC 60079-14
ATEX
Underwriting Group
FM (Factory Mutual)
CSA (Canadian Standards)
ATEX
Type 3R - TAF, TDF upright position
TFA - CL I, Div 2 wiring per NEC ANSI/NPFA 70 for
installation without wiring parameters. TDF, TTF, TRF
require an enclosure.
For dry locations and voltages less than 60Vdc, TTF &
TRF units must be in an enclosure.
TA, TJ & TD6000 with "W" option are NEMA 4/IP65 Rated.
TD6000 version requires shelter from direct sunlight.
Where loop voltages exceed 60Vdc (dry locations) or
30Vdc (potentially damp locations), the TTF and TRF
versions must be installed meeting the electrical shock
and fire protection requirements of ANSI/ISA S82.01.
Code
Drawing Number
EC-16984
EC-18005
EC-18007