ATEX Approvals:
Intrinsically Safe: 4-20 mA only
Catalog Version: TAEI7800, TDEI7800
Sira 02ATEX2013X
Ex ia IIB T4 Ga (Ta = -40°C to +80°C)
Ex ia IIIC T90°C Da (Ta = -40°C to +80°C) II 1D (T90°C)
Enclosure IP65
Catalog Versions: TTEI7800, TREI7800
Ex ia IIB T4 Ga (Ta = -40°C to +80°C)
IECEx Approvals:
IECEx SIR 08.0130X
Catalog Version: TAEI7800, TDEI7800
Ex ia IIB T4 Ga (Ta = -40°C to +80°C)
Ex ia IIIC T90°C Da (Ta = -40°C to +80°C)
Enclosure IP65
Catalog Versions: TTEI7800, TREI7800
Ex ia IIB T4 Ga (Ta = -40°C to +80°C)
Transducer Parameters
Umax
(U
)
1
28 V
i
Imax
(I
)
2
100 mA
i
1
Umax = Maximum Voltage
2
Imax = Maximum Current

HAZARDOUS LOCATIONS

Special Conditions for Safe Use - WARNINGS
1. Under certain extreme circumstances, the non-metallic parts incorporated in the enclosure of equipment,
TDEI7800 series may generate an ignition-capable level of electrostatic charge. Therefore the equipment shall
not be installed in a location where the external conditions are conducive to the build-up of electrostatic charge
on such surfaces. This is particularly important if the equipment is installed in a Zone 0/Division 1 location. In
addition, the equipment shall only be cleaned with a damp cloth. This is particularly important if the equipment
is installed in a Zone 0/Division 1 location.
2. The enclosure of the equipment; TD_I7800 series contains non-metallic materials that shall be protected from
UV light (for example, daylight or light from luminaries) when installed.
3. The enclosure of equipment; TD_I7800 and TA_I7800 series are manufactured from aluminum alloy. In
rare cases, ignition sources due to impact and friction sparks could occur. This shall be considered during
installation, particularly if the equipment is installed in a Zone 0/Division 1 location.
4. The enclosure of equipment; TD_I7800 and TA_I7800 series are capable of withstanding only low risk of
mechanical danger and hence additional protection shall be provided to ensure that it cannot be subjected to
extreme mechanical stress.
5. The DIN socket connected to TD_I7800 series shall comply with IP65 requirements.
6. The conduit connected to the enclosure of TA_I7800 shall maintain the IP65 requirements of the enclosure.
7. TT_I7800 and TR_I7800 shall be installed in an enclosure that maintains an ingress protection rating of at least
IP20/NEMA 1 and meet the enclosure requirements of IEC 60079-0 for Group II equipment.
The information set forth in the foregoing Installation, Operation and Maintenance Instructions shall not be modified or
amended in any respect without prior written consent of Fairchild Industrial Products Company. In addition, the information
set forth herein shall be furnished with each product sold incorporating Fairchild's unit as a component thereof.
HAZARDOUS AREA CLASSIFICATION
II 1G (T4)
II 1G (T4)
ATEX, IECEx
Wmax
(W
)
3
0.7 W
i
Ceq
(C
)
4
12nF
i
Leq
(L
)
5
0
i
3
Wmax = Maximum Power
4
Ceq
= Capacitance
5
Leq
= Inductance
CONTINUED
Wiring in Hazardous Areas
Wiring in hazardous areas should be performed in
accordance with the table 1. and any local codes that
apply.
Table 1. Hazardous Location Wiring Practices.
Country
U.S.
Canada
Europe
Intrinsically Safe Connections
Refer to the latest revision of the indicated drawing.
Table 2. Intrinsically Safe Connections.
Underwriting Group
FM (Factory Mutual)
CSA (Canadian Standards)
ATEX

LEGAL NOTICE

8
Agency
Code
ANSI/ISA RP 12.6
FM
ANSI/NFPA 70 (NEC ®)
CED Part 1
CSA
EN 50 039, EN 60079-14,
ATEX
IEC 60079-14
Drawing Number
EC-18970
EC-18971
EC-18972