Installation and programming instructions
1
INTRODUCTION
These instructions sheets are valid for VIVO-T101
control boards and must be read along with the VIVO-
M101 instruction manuals.
2
DESCRIPTION
The VIVO-T101 control board is suitable for three-phase
operators and three-phase power supply facilities.
The characteristics of the VIVO-T101 control panels are
similar to VIVO-M101 control panels, with the
following differences:
3
INSTALLATION
Carry out the electrical installation as described in the
VIVO-M101 control board manual, bearing in mind that
the operators and power supply connection must be in
line with the diagram on the following page:
4

PROGRAMMING AND STARTUP

Carry out the programming as described in the VIVO-
M101 control board manual, bearing in mind that DIP8
must always be placed in OFF.
5

FAILURE DIAGNOSIS

Follow the instructions of the VIVO-M101 control board
manual, taking into account fuses F1, F2 and F3 of the
three-phase plate (see figure on the following page).
MSA-102/00
Bear in mind the safety warnings set out in the
VIVO-M101 manual.
• A three-phase plate has been added for
connection to the three-phase operators and
three-phase power supply.
• The "slowdown" function has been removed,
meaning DIP8 is reserved for future use and
must always be placed in OFF.
• Some components have changed.
• The software is specific.
Z
"Fig. 1 Power supply and operator connections".
O
IMPORTANT: DIP8 must always be OFF.
English
VIVO-T101 Control board
5