Kohler K-T9493 Guia De Instalacion página 4

Ocultar thumbs Ver también para K-T9493:
Tabla de contenido

Publicidad

Idiomas disponibles

Idiomas disponibles

Before You Begin (cont.)
Factory calibrated inlet conditions are: Hot and cold water
pressure = 43-1/2 psi (3 kg/cm) Hot water supply temperature
= 149° F (65° C) Cold water supply temperature = 59° F (15° C).
If inlet conditions differ from those used during factory
calibration, it may be necessary to re-calibrate the valve after
installation. The installer must check the mixed flow
temperature after installation, and adjust the valve as needed
according to the instructions.
Kohler Co. reserves the right to make revisions in the design of
products without notice, as specified in the price book.
1012606-2-B
4
Kohler Co.

Publicidad

Tabla de contenido
loading

Este manual también es adecuado para:

K-t9494K-t9493-7K-t9493-4K-t9494-7

Tabla de contenido